leverd
New Member
- Thread starter
- #1
Hi Folks,
My Rivian wall charger is being replaced because I have been plagued with the "charging slowed issue" and RIvian provided the following instructions. My local installer who recently replaced my panel (400A) is providing (I think) conflicting installation information. The wire to the wall charger is 6AWG NM-B.
Please help me sort through what needs to be done.
Rivian says:
You'll want to be to be within the 90 degree column. Per NEC (210.19 (A)(1), conductors for fixed-in-place appliances that are expected to run at a maximum current for 3 hours or more, must be sized at least 125% of the appliance’s maximum load. For a 48-amp EV charger like the Rivian Wall Charger, the conductor needs to be able to handle at least 60 amps continuously. If you're within the 75 degree this will not cover the 125% if you're using a 60amp breaker, if this is what you're doing I would recommend charging at no more than 40 amps during your sessions.
My local installer says
On the chart, we need to go by the 75* column since the lugs on the circuit breaker are rated at 75*. (This is standard across all circuit breaker brands). According to this chart, at 75*, #6 Copper with THHN-THW insulation will deliver up to 65A continuous load. In summary, from the NEC table, #6 is the correct size wire.
What’s the right thing to do given that I am not inclined to replace/upgrade my new panel.
Please help. Thanks!
My Rivian wall charger is being replaced because I have been plagued with the "charging slowed issue" and RIvian provided the following instructions. My local installer who recently replaced my panel (400A) is providing (I think) conflicting installation information. The wire to the wall charger is 6AWG NM-B.
Please help me sort through what needs to be done.
Rivian says:
You'll want to be to be within the 90 degree column. Per NEC (210.19 (A)(1), conductors for fixed-in-place appliances that are expected to run at a maximum current for 3 hours or more, must be sized at least 125% of the appliance’s maximum load. For a 48-amp EV charger like the Rivian Wall Charger, the conductor needs to be able to handle at least 60 amps continuously. If you're within the 75 degree this will not cover the 125% if you're using a 60amp breaker, if this is what you're doing I would recommend charging at no more than 40 amps during your sessions.
My local installer says
On the chart, we need to go by the 75* column since the lugs on the circuit breaker are rated at 75*. (This is standard across all circuit breaker brands). According to this chart, at 75*, #6 Copper with THHN-THW insulation will deliver up to 65A continuous load. In summary, from the NEC table, #6 is the correct size wire.
What’s the right thing to do given that I am not inclined to replace/upgrade my new panel.
Please help. Thanks!