A licensed Electrician will be helping me to install my EVSE about a 35 foot run from the subpanel in my garage. He wants to use 6AWG romex on a 60 amp breaker for what will be, I hope, charging if needed at 48A.
Been reviewing the forms here and still the safest option is not clear to me. 6AWG romex is rated at 55 amps. Some say you must use a wire that is rated for 60A for a 60A breaker. Some say the charger will never pull more than 48A so it is safe.
6 AWG THHN appears to to be rated at 65 Ampacity but my electrician says that 6AWG will actually run hotter in a conduit even of appropriate diameter. I had thought the opposite.
I can easly run a cable or conduit.
Any advice would be appreciated.
Go with 6AWG romex ?
Go with 4AWG romex 70 ampacity (many say it fits in the charger connector) ?
Go with conduit ?
TIA
Been reviewing the forms here and still the safest option is not clear to me. 6AWG romex is rated at 55 amps. Some say you must use a wire that is rated for 60A for a 60A breaker. Some say the charger will never pull more than 48A so it is safe.
6 AWG THHN appears to to be rated at 65 Ampacity but my electrician says that 6AWG will actually run hotter in a conduit even of appropriate diameter. I had thought the opposite.
I can easly run a cable or conduit.
Any advice would be appreciated.
Go with 6AWG romex ?
Go with 4AWG romex 70 ampacity (many say it fits in the charger connector) ?
Go with conduit ?
TIA