In a nutshell, it’s the “continuous load” rule 215.2(A)(1) that trumps the “next size up” rule 240.4(B). The maximum ampacity of #6 Romex is 55amps. Since an EVSE is “continuous load”, rule says you must multiply 48A load by 125%=60amps, too much for 55ampacity #6 Romex.I'm not an electrician, but if the code for sizing says it can run 48A if the wire is rated for 90C I can't really see the difference. Again, I'm not an electrician but I did have a licensed electrician tell me it was fine.
At least that’s what my bartender told me. YBTMV (your bartender may vary).