I am struggling to understand why my 2023 R1T Dual Max Performance doesn't charge above 10kW on the Tesla universal wall charger or the Autel Maxicharge 50A EV charger. I also have an EVIQO EV charger that the truck is able to pull 10.8kW consistently during every charge, but for some reason, it will not pull more than 9.8kW from the Tesla or Autel chargers even though they are both configured for the max charge rate and are on a 60A breaker.

I have the EVIQO charger at one of my residences, but went with the Tesla charger at another residence. When I realized the truck was not charging at the max rate for 50A EV charger, I researched and found similar experiences from other Rivian owners.I decided to try the Autel 50A charger instead, and again, installed it the same 60A breaker that the Tesla universal wall charger was wired to before. I saw a lot of good reviews on the Autel, but so far in my experience, it's not charging any faster than the Tesla charger.
The EVIQO charger is by far the most economical charger here, yet the truck is able to pull almost 11 kW from it without issue, consistently.
I went with the Tesla mainly for the built in universal connector and then with the Autel for the RFID card feature. Unfortunately, it looks like the premium EV chargers provide a lesser charging experience than the budget charger.
There are many EV owners reporting awesome success with the Tesla and Autel chargers, both with Tesla's and Rivians, but I don't know why my experience is different. And yes, the charge amp setting in my R1T is set to 48A.
I am aware of the home charging bug, but unless I misunderstand it, it seems to be affecting Gen 2, not Gen 1 R1's.

I am about to return both the Tesla and Autel charges and get another EVIQO charger, but I prefer the Telsa and Autel for the aforementioned reasons.

Am I doing something wrong or am I missing something obvious here?

Rivian R1T R1S GEN 1 R1T Home Charging Frustrations Tesla 9.7kWh
Rivian R1T R1S GEN 1 R1T Home Charging Frustrations EVIQO 10.7kWh
Rivian R1T R1S GEN 1 R1T Home Charging Frustrations Autel 9.7kWh

Rivian R1T R1S GEN 1 R1T Home Charging Frustrations IMG_2577
Sponsored

 

VSG

Well-Known Member
Joined
Oct 3, 2022
Threads
4
Messages
3,319
Reaction score
6,259
Location
WA
Vehicles
R1T LE/RB/OC/20
What's your voltage? Did you install these yourself? Are you using an adapter?
 

mkhuffman

Well-Known Member
First Name
Mike
Joined
Nov 9, 2020
Threads
14
Messages
2,968
Reaction score
3,364
Location
Virginia
Vehicles
2025 R1T Tri-Max, Jeep GC-L, VW Jetta
It would be helpful to know how you installed the various EVSEs. Also, what is the charger pulling from the breaker box? Can you measure that?

I am sure you know there are losses in the charging process. I am charging at 48 Amps right now, and this is what the Rivian app reports :

Rivian R1T R1S GEN 1 R1T Home Charging Frustrations 1000003414


This is what is is getting supplied to the EVSE:

Rivian R1T R1S GEN 1 R1T Home Charging Frustrations 1000003411
 

godfodder0901

Well-Known Member
First Name
Jared
Joined
Mar 12, 2019
Threads
27
Messages
5,782
Reaction score
10,174
Location
Washington
Vehicles
2022 Rivian R1T LE
It would be helpful to know how you installed the various EVSEs. Also, what is the charger pulling from the breaker box? Can you measure that?

I am sure you know there are losses in the charging process. I am charging at 48 Amps right now, and this is what the Rivian app reports :

1000003414.webp


This is what is is getting supplied to the EVSE:

1000003411.webp
I pull 11.2-11.3 consistently at 48A.
 
OP
OP
lmerani

lmerani

Active Member
Joined
Nov 26, 2023
Threads
6
Messages
34
Reaction score
29
Location
Indiana
Vehicles
R1T Dual Perf. Max | 3rd Gen 4Runner 5spd Manual
What's your voltage? Did you install these yourself? Are you using an adapter?
I had the Tesla charger professionally installed. The install included the 60A breaker, conduit, wiring, disconnect box outside and the EV charger.
I did the Autel swap myself.

Here are the voltages while the charger is charging.
Line 1 - 120.6V
Line 2 - 119.5V
207.1V across both lines.
Rivian R1T R1S GEN 1 R1T Home Charging Frustrations IMG_2588
Rivian R1T R1S GEN 1 R1T Home Charging Frustrations IMG_2589
Rivian R1T R1S GEN 1 R1T Home Charging Frustrations IMG_2590
Rivian R1T R1S GEN 1 R1T Home Charging Frustrations IMG_2587
 

Sponsored

OP
OP
lmerani

lmerani

Active Member
Joined
Nov 26, 2023
Threads
6
Messages
34
Reaction score
29
Location
Indiana
Vehicles
R1T Dual Perf. Max | 3rd Gen 4Runner 5spd Manual
What's your voltage? Did you install these yourself? Are you using an adapter?
The Autel comes with the J1772 plug, so no adapter is required.
For the Tesla charger, I just used the built in J1772 adapter.
 

bfilippo

Well-Known Member
First Name
Benjamin
Joined
Sep 16, 2024
Threads
39
Messages
682
Reaction score
694
Location
Downeast Maine
Vehicles
2022 Launch Edition R1S Limestone, 2026 Gen2 R1T Tri Max AT, Storm Blue
Occupation
Consultant
Hmm, that is strange, but it does seem that YMMV. I have the 3rd gen Tesla wall charger from our former MYLR (non-universal), and utilize the j1772 adapter from A2Z on our Gen 1 and then no adapter on my Gen2 with NACS. I pretty consistently get 10.7kw on both vehicles at 48amps on 60amp breaker.
 

RickRivian

Well-Known Member
Joined
Dec 16, 2025
Threads
1
Messages
56
Reaction score
49
Location
SE MI
Vehicles
'22 Lightning ER Lariat,'22 Mach-E Premium 4X
Not an electrician, but 207v x 48amps = 9.9kW. 240v x 48 = 11.5kW. That is at the house, before ~7% loss.

Is this at a commercial building?
 
OP
OP
lmerani

lmerani

Active Member
Joined
Nov 26, 2023
Threads
6
Messages
34
Reaction score
29
Location
Indiana
Vehicles
R1T Dual Perf. Max | 3rd Gen 4Runner 5spd Manual
It would be helpful to know how you installed the various EVSEs. Also, what is the charger pulling from the breaker box? Can you measure that?

I am sure you know there are losses in the charging process. I am charging at 48 Amps right now, and this is what the Rivian app reports :

1000003414.webp


This is what is is getting supplied to the EVSE:

1000003411.webp
I fully expect some losses
Not an electrician, but 207v x 48amps = 9.9kW. 240v x 48 = 11.5kW. That is at the house, before ~7% loss.

Is this at a commercial building?
It's a shop on our property and it was wired for 3 phase. This makes sense. Not a charger or Rivian issue then. Since it has 3 phase, I should have just installed a DC charger instead. 😄
 

hudesigns

Well-Known Member
First Name
Jim
Joined
May 27, 2024
Threads
5
Messages
131
Reaction score
110
Location
New York
Vehicles
2026 R1S dual max performance
I had the Tesla charger professionally installed. The install included the 60A breaker, conduit, wiring, disconnect box outside and the EV charger.
I did the Autel swap myself.

Here are the voltages while the charger is charging.
Line 1 - 120.6V
Line 2 - 119.5V
207.1V across both lines.
IMG_2587.webp
207V seems low. I might not be correct but when I charge using Grizzle mini 40A charger the average voltage is 236V and get bit above 9kw. Your 207V x 48A= 9.9kw with some loss it should be around 9.6kw. Maybe you take a voltage test when EVIQO is charging to see what voltage is pulls.
Rivian R1T R1S GEN 1 R1T Home Charging Frustrations IMG_9411
 

Sponsored

mkhuffman

Well-Known Member
First Name
Mike
Joined
Nov 9, 2020
Threads
14
Messages
2,968
Reaction score
3,364
Location
Virginia
Vehicles
2025 R1T Tri-Max, Jeep GC-L, VW Jetta
I fully expect some losses

It's a shop on our property and it was wired for 3 phase. This makes sense. Not a charger or Rivian issue then. Since it has 3 phase, I should have just installed a DC charger instead. 😄
Install a DC charger that can also tap into the battery so you can do VTBuilding (not VTH, since it is not your home). I would love to do that but $10-20k just doesn't seem worth it right now. It might even be more since I only have 200 Amp service.
 

RickRivian

Well-Known Member
Joined
Dec 16, 2025
Threads
1
Messages
56
Reaction score
49
Location
SE MI
Vehicles
'22 Lightning ER Lariat,'22 Mach-E Premium 4X
I fully expect some losses

It's a shop on our property and it was wired for 3 phase. This makes sense. Not a charger or Rivian issue then. Since it has 3 phase, I should have just installed a DC charger instead. 😄
3 phase is the answer. Simple math.
 

Erik+

Well-Known Member
First Name
Erik
Joined
Sep 2, 2024
Threads
5
Messages
365
Reaction score
567
Location
Colorado
Vehicles
2023 R1T
Occupation
Engineering
You should be getting above 237V or so and it looks like you are only pulling 207V. I would work from the panel back out to the charger and see what readings you are getting. Chances may be that the voltage drop is occurring well upstream of your chargers.
 
OP
OP
lmerani

lmerani

Active Member
Joined
Nov 26, 2023
Threads
6
Messages
34
Reaction score
29
Location
Indiana
Vehicles
R1T Dual Perf. Max | 3rd Gen 4Runner 5spd Manual
I am going to ask the electrician to look at it again just to be certain, but based on the comments here and the math, it appears to be the nature of 3 phase power. I am fine with the lower power numbers this as long as it's not a charger or vehicle issue.
 

VandalSibs

Well-Known Member
First Name
Andrew
Joined
Dec 27, 2023
Threads
15
Messages
1,449
Reaction score
2,550
Location
Eastern Washington State
Website
www.sibulskymusic.com
Vehicles
R1T Dual Motor Large Pack
Occupation
Composer, IT Service Desk Analyst
Clubs
 
I am going to ask the electrician to look at it again just to be certain, but based on the comments here and the math, it appears to be the nature of 3 phase power. I am fine with the lower power numbers this as long as it's not a charger or vehicle issue.
No need to call the electrician - it's very much because of three-phase power. You see the same kind of voltages with Level 2 chargers at parking garages and other commercial buildings because of that.

The DC option would be interesting, but has been mentioned it's really expensive for what you are getting (only about 25kW from what I'm seeing in a quick "I'm just getting clocked in at work" search).