I have an Emporia Pro EVSE that I’ve been using without problem for about a year. It’s wired to a 50A breaker, and set to pull a max of 40A, with one of their power monitors to keep it from drawing too much when there’s other large loads.
Last night, for the first time ever, it tripped the breaker, after charging for several hours. It was still about 20% away from my set SoC, so I gave it some time, the reset the breaker to continue charging. A couple hours later it tripped the breaker again.
It’s tripping its own breaker, not the main one for the sub-panel it’s in, and nothing else seems to be having any issues. Looking at the logs, at the time it tripped it was pulling right about 40A (more like 39.7) for a sustained period.
I was already in bed when it tripped the second time, so it’s still off, but my plan it to adjust the settings to 35A max, and try again.
Is there anything else I should be looking at? Could the breaker itself be wearing out after only a year of use (with several months of zero use when we weren’t here)? I’ve already got an electrician coming in for some other work soon (same guy who installed this in the first place), so I can have him take a look at it, too. Maybe replace the 50A breaker with a 60A for a little extra margin.
Last night, for the first time ever, it tripped the breaker, after charging for several hours. It was still about 20% away from my set SoC, so I gave it some time, the reset the breaker to continue charging. A couple hours later it tripped the breaker again.
It’s tripping its own breaker, not the main one for the sub-panel it’s in, and nothing else seems to be having any issues. Looking at the logs, at the time it tripped it was pulling right about 40A (more like 39.7) for a sustained period.
I was already in bed when it tripped the second time, so it’s still off, but my plan it to adjust the settings to 35A max, and try again.
Is there anything else I should be looking at? Could the breaker itself be wearing out after only a year of use (with several months of zero use when we weren’t here)? I’ve already got an electrician coming in for some other work soon (same guy who installed this in the first place), so I can have him take a look at it, too. Maybe replace the 50A breaker with a 60A for a little extra margin.