I've got some experience with sizing of refrigeration systems which is really what we are dealing with here. Systems are designed as, well, a "balanced system". If the problem is that the system is properly designed but undersized for the BTU load (such as underestimating the heat load created by the greenhouse roof in the R1S at 110 degrees ambient), just Increasing the compressor size likely won't fix this type of problem. All of the components - lines sizes (tubing), evaporator and condensor coils, thermal expansion valve or capillary tube, etc. all need to be resized. The only thing a new compressor would fix is if they somehow undersized it in the original design, but since it works fine for many people at or under 100 degrees, I think it's an overall system BTU capacity issue. The other possibility is that it was designed correctly but an OEM is not delivering components to spec.
Thanks for the clear explanation. Guess there are not much rivian can do to improve this