Rivian EVSE and 4 AWG
tiltedandsaltyaf
Los Angeles, CA
There's a nice cutout in the rear of the EVSE... I don't understand why more people aren't using it!
drywall work required, a lot easier to go in from the bottom
CommodoreAmiga
INACTIVE
INACTIVE
Pic OP posted shows a LB conduit body. It's unlikely any drywall work would have been required to fish it the extra ~2 feet higher.
Edit: I guess OP has a firebreak in that exact spot. Unfortunate. My point stands, however... I've seen a lot of Rivian EVSE installations with external conduit that appears unnecessary. This case may have been necessary, but I'm sure many of the others were not.
seatosummit
Austin
Santa Barbara, CA
'22 R1T, '87 LJ70, 73' Porsche 914 (EV Conversion)
Electrical Engineer
The odd 30 degree screw terminal orientation on the PCB of that EVSE drives me nuts.
This touches on a sometimes overlooked electrical code violation by DIY. For future reference for those doing an install, it's a violation of NEC to install a junction box, condulet, etc. in the wall and cover it up with drywall or other building material. You need to use the appropriate 90 degree fitting if the wall is enclosing the fitting, or install a flush mount junction/pull box. You don't want the inspector (if actually being done, lol) forcing you to rip the wall apart to remedy it if he/she sees a condulet coming in the back of the enclosure. The only exception to this that I am aware of is drop ceilings, as the panels are readily removable. It's generally OK to have boxes/condulets above a drop ceiling.
314.29 Boxes, Conduit Bodies, and Handhole Enclosures to Be Accessible. Boxes, conduit bodies, and handhole enclosures shall be installed so that wiring contained in them can be rendered accessible in accordance with 314.29(A) and (B).
N 314.29(A) In Buildings and Other Structures. Boxes and conduit bodies shall be installed so the contained wiring can be accessed without removing any part of the building or structure.
N 314.29(B) Underground. Underground boxes and handhole enclosures shall be installed so they are accessible without excavating sidewalks, paving, earth, or other substance that is to be used to establish the finished grade.
CommodoreAmiga
INACTIVE
INACTIVE
Yes, fair points. I ran conduit to a 4" box mounted behind my EVSE, then marked and drilled a flat cover and used a chase nipple to transition into the EVSE. The inspector liked it.
That's a great idea, and it actually fits with another implied exception in the code. A permanent light fixture that is being supplied power can cover the junction box. A strict interpretation might be that the light fixture, or in your case the EVSE, violates "without removing any part of the building or structure." If it is a permanent light fixture, is it part of the building? Fortunately, common sense prevails with respect to this!