Sponsored

Charger Circuit Breaker Type

pdiemen

Member
First Name
Paul
Joined
Dec 23, 2023
Threads
3
Messages
9
Reaction score
2
Location
California
Vehicles
Rivian R1S
I will be installing the Rivian Wall charger with 6 AWG copper wires for maximum home charging. There are two types of 60 amp circuit breakers available, a QP and QPH. Which one should I be using?
Sponsored

 

SparkyR1t

Well-Known Member
Joined
Apr 5, 2023
Threads
2
Messages
380
Reaction score
388
Location
Chicago
Vehicles
R1t/Model Y
Occupation
Retired Commercial Electrician and mechanic
Has to do with short circuit interrupting current capability. For a residential application QP is probably best. You can upgrade to QPH if necessary but not all panels are designed to handle the higher short circuit currents. But we are not expecting a short circuit to occur in most cases
 
OP
OP

pdiemen

Member
First Name
Paul
Joined
Dec 23, 2023
Threads
3
Messages
9
Reaction score
2
Location
California
Vehicles
Rivian R1S
The Rivian installation guide says 6 gauge for 60 amps and 8 gauge for 50 amp breaker.
 

DevSecOps

Well-Known Member
First Name
Todd
Joined
Apr 16, 2023
Threads
2
Messages
170
Reaction score
412
Location
Sacramento, CA
Vehicles
2023 R1T, 2023 M3P, 2021 Audi SQ5
Occupation
CISO
Clubs
 
50amp breaker for 6g wire?
The Rivian installation guide says 6 gauge for 60 amps and 8 gauge for 50 amp breaker.
You can use 6awg THHN for 60A, but it would need to 4awg if you go NM. If they are running conduit and individual conductors then 6awg would be fine. If it's in a shielded bundle then it would have to be 4/3 (4awg) for 60A.