Keep in mind that if you're using Romex and not THHN in conduit, this is just good for a 50A circuit for 40A charging. You need to drop to 4awg if you're using Romex and want to put it on a 60A circuit. Not worth the increase just for 20% faster charging IMO. 40A charging is plenty. Being that this is in a garage of a high rise, he's probably using conduit anyway.
Sponsored

 

Greg Chick

Well-Known Member
First Name
Greg
Joined
Jan 27, 2023
Threads
12
Messages
916
Reaction score
654
Location
Tehachapi Ca. 93561
Website
diyplumbingadvice.com
Vehicles
R1T Quad, large battery, 21" Adventure
Occupation
Retired Plumbing Contractor
Clubs
 
Your electrician isn't wrong, he's doing the right thing by considering voltage drop. But in your case it's not significant. #6 at 1.42% voltage drop is still well under NEC maximum of 3%. Considering that #4 costs more and if done right, he needs provide approved transition from #4 to #6 which will also add to the cost.

I would measure the line voltage at the panel. It may be higher or lower than than 240v. I'd just go with #6 as long as the line voltage is at least 238 volts at the panel.

1774636449332-eh.webp
I have used stranded wire and cut off a few strands to fit the terminal. Also once the stranded wire fits in, pulled it out and soldered it to the shape that fits then reinserted it and clamped tight. Also, I have put my load on it, them tested the voltage drop to see that it is above the Min.
Another point is using a new breaker that is top grade listed for EV or long load not just 10 min. load.
 

therealcmj

Well-Known Member
First Name
Chris
Joined
Oct 5, 2024
Threads
3
Messages
197
Reaction score
245
Location
Boston, MA
Vehicles
2025 R1S
I have used stranded wire and cut off a few strands to fit the terminal. Also once the stranded wire fits in, pulled it out and soldered it to the shape that fits then reinserted it and clamped tight.
That seems very not good. Like very very.
 
OP
OP

R1S88

Well-Known Member
Joined
Dec 14, 2022
Threads
24
Messages
214
Reaction score
216
Location
Massachusetts
Vehicles
R1S
Clubs
 
Still not worth it.

Keep in mind that if you're using Romex and not THHN in conduit, this is just good for a 50A circuit for 40A charging. You need to drop to 4awg if you're using Romex and want to put it on a 60A circuit. Not worth the increase just for 20% faster charging IMO. 40A charging is plenty. Being that this is in a garage of a high rise, he's probably using conduit anyway.
I'm pretty sure it's THHN in conduit, but would stress that I would be very happy to have 20% faster as cost is not a consideration in this specific case. Thanks
 

Zoidz

Well-Known Member
First Name
Gil
Joined
Feb 28, 2021
Threads
227
Messages
5,218
Reaction score
11,737
Location
PA
Vehicles
23 R1S Adv, Avalanche, BMWs-X3,330cic,K1200RS bike
Occupation
Engineer
I have used stranded wire and cut off a few strands to fit the terminal. Also once the stranded wire fits in, pulled it out and soldered it to the shape that fits then reinserted it and clamped tight. Also, I have put my load on it, them tested the voltage drop to see that it is above the Min.
Another point is using a new breaker that is top grade listed for EV or long load not just 10 min. load.
Yes, that's a common work around. Yes, it's very low risk of any complications. But ... if the installation gets inspected, that technique violates several sections of NEC Article 110 and should/would fail inspection by a competent electrical inspector. There are reducing splice fittings/terminals made for this purpose.
 

Sponsored

Greg Chick

Well-Known Member
First Name
Greg
Joined
Jan 27, 2023
Threads
12
Messages
916
Reaction score
654
Location
Tehachapi Ca. 93561
Website
diyplumbingadvice.com
Vehicles
R1T Quad, large battery, 21" Adventure
Occupation
Retired Plumbing Contractor
Clubs
 
Yes, that's a common work around. Yes, it's very low risk of any complications. But ... if the installation gets inspected, that technique violates several sections of NEC Article 110 and should/would fail inspection by a competent electrical inspector. There are reducing splice fittings/terminals made for this purpose.

I have seen the copper ones, that would be Much better, I agree. Again, imposing full load, then measuring the volt insuring the drop is minimal and within code.
 

beatle

Well-Known Member
Joined
Jun 20, 2024
Threads
17
Messages
1,149
Reaction score
1,566
Location
Springfield, VA
Vehicles
'23 R1T PDM Max, '97/'25 Miatas
Occupation
IT
Clubs
 
Yes, that's a common work around. Yes, it's very low risk of any complications. But ... if the installation gets inspected, that technique violates several sections of NEC Article 110 and should/would fail inspection by a competent electrical inspector. There are reducing splice fittings/terminals made for this purpose.
I've also done it the hacky way on car stereo installs, but yes, these are better:

https://www.elecdirect.com/lug-comp...educing-crimp-splice-4-awg-gray-to-6-awg-blue

Rivian R1T R1S Wall charger wire gauge question 1774713154898-24



I'm pretty sure it's THHN in conduit, but would stress that I would be very happy to have 20% faster as cost is not a consideration in this specific case. Thanks
Oh for sure, if he's already doing 6awg THHN in conduit, might as well charge at 48A.
 

Zoidz

Well-Known Member
First Name
Gil
Joined
Feb 28, 2021
Threads
227
Messages
5,218
Reaction score
11,737
Location
PA
Vehicles
23 R1S Adv, Avalanche, BMWs-X3,330cic,K1200RS bike
Occupation
Engineer
I have seen the copper ones, that would be Much better, I agree. Again, imposing full load, then measuring the volt insuring the drop is minimal and within code.
An inspector could fail the trimming technique for several code violations:
- The EVSE specifies acceptable wire size range for the termination. The attached wire indicates #4, outside of the EVSE specified design range
- The wire indicates #4 on the jacket, trimming compromises the integrity of the jacket label vs wire ampacity. A future person could install a larger breaker and load requiring #4 with potential consequences.
- They can fail if they see the stripping technique has damaged the conductor. I've seen them do this on solid wires that are nicked while stripping. Picky, yes, but they can and will fail it.

I'm not finding fault with anyone doing this, just pointing out the possible issues that could come up if the installation is inspected.
 

Zoidz

Well-Known Member
First Name
Gil
Joined
Feb 28, 2021
Threads
227
Messages
5,218
Reaction score
11,737
Location
PA
Vehicles
23 R1S Adv, Avalanche, BMWs-X3,330cic,K1200RS bike
Occupation
Engineer
Update: I was given a more accurate measurement and it’s actually 130 feet. I suspect the answer is still to go with 6 awg, but thought I would ask the experts here to be sure. Thanks!
Still within NEC under 3%, I would run #6 and avoid the other issues.
Or..... go bigger by installing a 100A subpanel if there is the possiblity of future loads, and then that easily transitions to a short #6 for your EVSE. That was my solution. I now have a 100A subpanel in the garage.

Rivian R1T R1S Wall charger wire gauge question 1774714372181-ex
 

Greg Chick

Well-Known Member
First Name
Greg
Joined
Jan 27, 2023
Threads
12
Messages
916
Reaction score
654
Location
Tehachapi Ca. 93561
Website
diyplumbingadvice.com
Vehicles
R1T Quad, large battery, 21" Adventure
Occupation
Retired Plumbing Contractor
Clubs
 
An inspector could fail the trimming technique for several code violations:
- The EVSE specifies acceptable wire size range for the termination. The attached wire indicates #4, outside of the EVSE specified design range
- The wire indicates #4 on the jacket, trimming compromises the integrity of the jacket label vs wire ampacity. A future person could install a larger breaker and load requiring #4 with potential consequences.
- They can fail if they see the stripping technique has damaged the conductor. I've seen them do this on solid wires that are nicked while stripping. Picky, yes, but they can and will fail it.

I'm not finding fault with anyone doing this, just pointing out the possible issues that could come up if the installation is inspected.
Good points
 

Sponsored

Tlohrenz

Well-Known Member
First Name
Tim
Joined
Jun 16, 2024
Threads
17
Messages
76
Reaction score
53
Location
Golden, CO
Vehicles
2023 Rivian R1T
Occupation
Retired
That 130 ft distance requires 5 gauge, so you'll need 4 gauge copper. You can run 4 gauge wire to a small 2 or 4 space sub-panel. Then 6 gauge to the charger. That will pass anyone's code and give you max voltage.
this is what I ended up doing.
 

Conseil

Well-Known Member
First Name
John
Joined
Apr 26, 2024
Threads
3
Messages
45
Reaction score
18
Location
California
Vehicles
2025 R1T G2, 2008 Tacoma for sale
Occupation
Retired Engineer
Your electrician isn't wrong, he's doing the right thing by considering voltage drop. But in your case it's not significant. #6 at 1.42% voltage drop is still well under NEC maximum of 3%. Considering that #4 costs more and if done right, he needs provide approved transition from #4 to #6 which will also add to the cost.

I would measure the line voltage at the panel. It may be higher or lower than than 240v. I'd just go with #6 as long as the line voltage is at least 238 volts at the panel.