There are a couple of options for this wire size issue. In all cases the breaker must be rated for the #6 wire, not the #4:This detail is key for the OP. The ChargePoint Home Flex can accept a maximum of 6 AWG so 4 AWG into the ChargePoint is not an option. This is also why hard wiring the ChagePoint for 48A charging requires 6 AWG THHN instead of NM-B (Romex).
![]()
Edit: I am most definitely not an electrician so not sure about compliance on this but it may be possible to run 4 AWG to a junction box near the charger and then run 6 AWG wire to the Home Flex from there. You'd definitely still be limited to a 60 A breaker in this scenario but if you needed more in the future, it would only require rewiring between the junction and the charger (likely to happen anyway if future EVSE comes with a pigtail) and swapping the breaker as opposed to replacing an entire 80 ft run.
1) As you mention, install a box and pigtail the #4 to #6. For this size wire, do it right by using the butt splice or split bolt , not wire nuts. This could possibly be done inside the EVSE if space permits.
2) If running #4 stranded wire THHN/THWN, you could remove a strand or two so that it just fits tightly under the #6 sized terminal. Yes, we could debate that removing too many strands will reduce the effective wire to less than #6. If that is concerning, just do #1 above.