Room COULD be made by moving the 20 SPB to a single side, however it comes down AWG of service wires that feed the box.You don’t have enough room on that bus bar for a double pole breaker. And it looks pretty well loaded already with what you have there. My advice, call an electrician.
Well saidEveryone calm down and stop scaring the OP. Yes, there are code violations, but that doesn't mean it is overloaded.
Could you pull the safety panels off the two exterior panels and give us pictures of that?
BTW, no one seems to have noticed that in the small panel that has four double pole breakers, that the single pole breakers aren't connected to anything. They can be taken out and you'd have room for a new double pole breaker. But yes, you'd want to do a load calculation because that is a lot of load there already.
How many amps do you want, the full 48A that the Rivian can handle?
I wouldn’t touch adding any load to that box until the conductors feeding the main lugs are fixed.additional details for the mystery box
![]()
Oops, I didn't even notice that a) this was your outside box (I had asked to see a picture of it before!) and b) those breakers on the left were OFF (but to be fair no one else is noticing much either ?).additional details for the mystery box
![]()