Sponsored

Testing the Rivian as a ‘backup’ power source

MountainBikeDude

Well-Known Member
First Name
Adam
Joined
Jun 20, 2019
Threads
55
Messages
3,354
Reaction score
7,152
Location
Vancouver
Vehicles
2023 El Cap Quad Motor R1T (Selling the Xterra)
Clubs
 
Are you able to target the output of the outlets through the display, I know you can turn them on and off, but is there a sub menu within that functionality?
Sponsored

 
OP
OP
jjswan33

jjswan33

Well-Known Member
First Name
Joshua
Joined
Sep 17, 2021
Threads
135
Messages
4,455
Reaction score
9,880
Location
Sandy, OR
Vehicles
Rivian R1T LE, Hyundai Ioniq 5 Limited
Occupation
Engineer
Clubs
 
Are you able to target the output of the outlets through the display, I know you can turn them on and off, but is there a sub menu within that functionality?
Not that I am aware of, I can’t even find any information about what is being drawn, a display showing power out would be useful.
 

the long way downunder

Well-Known Member
First Name
Adam
Joined
Jan 15, 2021
Threads
3
Messages
944
Reaction score
998
Location
charging
Vehicles
Tesla
Occupation
WFH
Almost certainly a ground loop. They ran into this at TFL trying to do the same thing with the Ford F150 (not the lightning, but still had power available). Check out this video about 2:30 in.
Right, I assume it's ground detection.
 

the long way downunder

Well-Known Member
First Name
Adam
Joined
Jan 15, 2021
Threads
3
Messages
944
Reaction score
998
Location
charging
Vehicles
Tesla
Occupation
WFH
Here's the info from the owner's manual. I'm sure if I take a watt meter and fan heater, it will deliver 1500W to a single outlet. I guess I could run it for an hour and then view the truck through a thermal camera and see what warms up … : )

Rivian R1T R1S Testing the Rivian as a ‘backup’ power source 1650156165534


Rivian R1T R1S Testing the Rivian as a ‘backup’ power source 1650156179412
 

Sponsored

lostpacket

Well-Known Member
Joined
Dec 4, 2021
Threads
25
Messages
735
Reaction score
2,187
Location
Vermont
Vehicles
Crosstrek, R1T
Occupation
Software Engineer
What are the chances this would be possible from the J1772/CCS port if you had an external inverter?

Also is there a way to bond the ground back to the truck's neutral? I am assuming the ground fault is being detected because the ground and neutral are bonded at the service entrance / panel?

(disclaimer: I am very much not an electrician, hence the possibly dumb questions)
 

Zoidz

Well-Known Member
First Name
Gil
Joined
Feb 28, 2021
Threads
227
Messages
5,251
Reaction score
11,805
Location
PA
Vehicles
23 R1S Adv, Avalanche, BMWs-X3,330cic,K1200RS bike
Occupation
Engineer
Inrush current can be 3 to 7 times the running current on a refrigeration compressor. That will exceed the rating of the Rivian inverter. Here's the electrical specs for a Tecumseh AE4440Y refrigeration compressor, this is typical of a full size home refrigerator. Note that while the Rated Load Amps (RLA) is 5.82 Amps, the Locked Rotor Amps (LRA) is 32A. On a cold start, the inrush current can approach the LRA in the first 100 to 200 milliseconds. That's almost certainly the problem. You won't see this surge on any consumer current monitor. It happens too fast. 2nd image is an example of the current at startup of a refrigeration compressor.

You could try putting a soft start inline with the refrigerator. That may or may not help.

Rivian R1T R1S Testing the Rivian as a ‘backup’ power source 1650167357412

Rivian R1T R1S Testing the Rivian as a ‘backup’ power source 1650167959624
 

the long way downunder

Well-Known Member
First Name
Adam
Joined
Jan 15, 2021
Threads
3
Messages
944
Reaction score
998
Location
charging
Vehicles
Tesla
Occupation
WFH
What are the chances this would be possible from the J1772/CCS port if you had an external inverter?

Also is there a way to bond the ground back to the truck's neutral? I am assuming the ground fault is being detected because the ground and neutral are bonded at the service entrance / panel?

(disclaimer: I am very much not an electrician, hence the possibly dumb questions)
That's "vehicle to load" or V2L (also V2X "anything" and V2G "grid" and V2V "vehicle" … it's all just taking shape.) If Rivian has built the right hardware into the truck, V2L is easy and requires only a dongle from CCS to a suitable connector to power a house (you can read about this as done by Ford with the Lightning or the F-150 Hybrid.)
A tech at Rivian told me the charge port is undergoing a complete redesign. Hopefully Rivian will offer V2L and I imagine the charge point is the logical/easy place to tap into power for a Rivian-designed winch (though I'm told the winch project was recently cancelled .)
 
OP
OP
jjswan33

jjswan33

Well-Known Member
First Name
Joshua
Joined
Sep 17, 2021
Threads
135
Messages
4,455
Reaction score
9,880
Location
Sandy, OR
Vehicles
Rivian R1T LE, Hyundai Ioniq 5 Limited
Occupation
Engineer
Clubs
 
Inrush current can be 3 to 7 times the running current on a refrigeration compressor. That will exceed the rating of the Rivian inverter. Here's the electrical specs for a Tecumseh AE4440Y refrigeration compressor, this is typical of a full size home refrigerator. Note that while the Rated Load Amps (RLA) is 5.82 Amps, the Locked Rotor Amps (LRA) is 32A. On a cold start, the inrush current can approach the LRA in the first 100 to 200 milliseconds. That's almost certainly the problem. You won't see this surge on any consumer current monitor. It happens too fast. 2nd image is an example of the current at startup of a refrigeration compressor.

You could try putting a soft start inline with the refrigerator. That may or may not help.

1650167357412.png

1650167959624.png
As I said in my follow up above the circuit on the Rivian trips even when there is no load as soon as it is connected to the transfer switch. So I presume it is the ground loop as proposed by @PAFDenver

.
 

pc500

Well-Known Member
Joined
Jun 22, 2021
Threads
20
Messages
1,045
Reaction score
563
Location
US
Vehicles
dodge ram
I tested 1750 watts and it worked fine. 2200 tripped it.

This was with a resistive load ie a hair dryer and space heater.

There's some buffer in there but it might not be as much as you need.

Although it's not the 2000 of your yeti I suppose it's probably tripping for other protective reasons unrelated to draw.
 

Sponsored

ajdelange

Well-Known Member
First Name
A. J.
Joined
Aug 1, 2019
Threads
9
Messages
2,883
Reaction score
2,319
Location
Virginia/Quebec
Vehicles
Tesla XLR+2019, Lexus, Landcruiser, R1T
Occupation
EE Retired
I did check and the truck will run my GZ battery charger but apparently it will only push my 600W charger at 355.7W.
That's about as fast as the 6kWh Yeti will accept charge so that can't be blamed on the truck. The big clue here is that the charger is isolated from ground (no earth pin on the plug) whereas the little transfer panel isn't. Thus the "system" is grounded in 2 places and a gfci trips.

You can still do what you want to do but you will have to get an isolation transformer ($$$).
 

ajdelange

Well-Known Member
First Name
A. J.
Joined
Aug 1, 2019
Threads
9
Messages
2,883
Reaction score
2,319
Location
Virginia/Quebec
Vehicles
Tesla XLR+2019, Lexus, Landcruiser, R1T
Occupation
EE Retired
It's probably an appropriate place to note that the Rivian is not intended for this sort of service. It's inverter is low power, single phase and apparently equipped with protective circuitry to prevent damage to itself if people try. Compare to the inverter in the CT or F150 which are much more robust biphase inverters intended to be able to operate hefty 240V loads at a construction site. The Rivian inverter is designed to run your Espresso machine at a glamping site.
 

Zoidz

Well-Known Member
First Name
Gil
Joined
Feb 28, 2021
Threads
227
Messages
5,251
Reaction score
11,805
Location
PA
Vehicles
23 R1S Adv, Avalanche, BMWs-X3,330cic,K1200RS bike
Occupation
Engineer
As I said in my follow up above the circuit on the Rivian trips even when there is no load as soon as it is connected to the transfer switch. So I presume it is the ground loop as proposed by @PAFDenver
It wasn't clear to me that the load was disconnected when you plugged in. Specifically, does it trip with the transfer set to Line, and all load breakers off?
 
OP
OP
jjswan33

jjswan33

Well-Known Member
First Name
Joshua
Joined
Sep 17, 2021
Threads
135
Messages
4,455
Reaction score
9,880
Location
Sandy, OR
Vehicles
Rivian R1T LE, Hyundai Ioniq 5 Limited
Occupation
Engineer
Clubs
 
It wasn't clear to me that the load was disconnected when you plugged in. Specifically, does it trip with the transfer set to Line, and all load breakers off?
Yes exactly.

So I investigated further the Rivian trips out as soon as you try to plug it into the Transfer switch. I tried both with the switch set to Gen and Line. I guess it is some sort of safety built in against this use case.
 
OP
OP
jjswan33

jjswan33

Well-Known Member
First Name
Joshua
Joined
Sep 17, 2021
Threads
135
Messages
4,455
Reaction score
9,880
Location
Sandy, OR
Vehicles
Rivian R1T LE, Hyundai Ioniq 5 Limited
Occupation
Engineer
Clubs
 
I tested 1750 watts and it worked fine. 2200 tripped it.

This was with a resistive load ie a hair dryer and space heater.

There's some buffer in there but it might not be as much as you need.

Although it's not the 2000 of your yeti I suppose it's probably tripping for other protective reasons unrelated to draw.
Yeah the GZ is 2000W but with 3500W surge I guess the Rivian is 1500W with some surge capacity to handle the inrush of things like a refrigerator or a power tool.

I will do further testing at some point, for my camping setup I will need to know whether I need to add a more powerful inverter.
Sponsored

 
 








Top