Was hoping for advice on how to proceed with my charging set up.
I have a 6-50 outlet (50 amps).
I have a rivian wall charger that I am going to have an electrician install. Should I have him convert that outlet and use the wires for the wall charger (I guess this would cap wall charger at 40 amps - with proper adjustments) OR should I leave the outlet there and have him create a new 60a circuit and install the wall charger above that outlet (I park right in front of that area). Thanks for your input!

Rivian R1T R1S Home Charging Advice IMG_2127.JPG
Sponsored

 

Christopher

Well-Known Member
First Name
Christopher
Joined
May 31, 2022
Threads
34
Messages
583
Reaction score
573
Location
South Florida
Vehicles
R1T
Occupation
Tech
Clubs
 
If you're going to be spending money on an electrician, I'd have them run a new circuit for the Rivian charger and keep the 6-50 and convert the 6-50 to 14-50. Always good to have.

New circuit would be a $15-$30 60a breaker and 6 feet of 4/3 NM-B for $75, plus 1hr labor.


Your panel and where the charger location are would be a very easy install.

If you don't want to spend anything, just cancel or return the Rivian charger and use the mobile charger to the existing 6-50 with an adapter
 
Last edited:

Cosmacelf

Well-Known Member
Joined
Nov 11, 2020
Threads
20
Messages
442
Reaction score
530
Location
San Diego, CA
Vehicles
Rivian R1S, Tesla Model X
Occupation
Software
Seems that the previous occupant had an EVSE that could be plugged into a 6-50 outlet. If you are paying full price for your Rivian EVSE, I’d recommend checking out other EVSEs that can plug into 6-50 receptacle and call it a day. 40A vs 48A charging isn’t a huge difference unless you routinely do a lot of driving.

Re-reading your post, it says you already have a Rivian wall charger. In that case, yeah, just install a new 60A circuit. Don’t get freaked out when he decides to use 6 gauge Romex, which is likely what he’ll use.

Alternatively, you could buy a 6-50 extension cord, chop off the receptacle end and connect it to the Rivian EVSE yourself, no electrician.
 
Last edited:

electruck

Well-Known Member
Joined
Oct 6, 2019
Threads
74
Messages
4,159
Reaction score
7,732
Location
Dallas, TX
Vehicles
2023 Rivian R1S
Sorry but 6/3 NM-B (Romex) does NOT meet code (inadequate temp spec) and should NOT be used to wire a 48A EVSE. No competent electrician should be using Romex for this. 6 AWG THHN through conduit would be a proper install for a short run like that.

Rivian R1T R1S Home Charging Advice riv_evse_wir
 

Christopher

Well-Known Member
First Name
Christopher
Joined
May 31, 2022
Threads
34
Messages
583
Reaction score
573
Location
South Florida
Vehicles
R1T
Occupation
Tech
Clubs
 
Sorry but 6/3 NM-B (Romex) does NOT meet code (inadequate temp spec) and should NOT be used to wire a 48A EVSE. No competent electrician should be using Romex for this. 6 AWG THHN through conduit would be a proper install for a short run like that.

riv_evse_wire.webp
I stand corrected, thank you. 6/3 would only allow for 44a so you'd have to dial back the charger or go to 4/3.

THHN/THWN in conduit would be unnecessary extra work running conduit since the panel is recessed in drywall and the run would be inside the drywall.
 

Sponsored

Tango45

Well-Known Member
First Name
Erik
Joined
Feb 15, 2021
Threads
6
Messages
596
Reaction score
1,494
Location
Northern VA
Vehicles
Ioniq 5, R1S
Clubs
 
If you're going to be spending money on an electrician, I'd have them run a new circuit for the Rivian charger and keep the 6-50 and convert the 6-50 to 14-50. Always good to have.

New circuit would be a $15-$30 60a breaker and 6 feet of 4/3 NM-B for $75, plus 1hr labor.


Your panel and where the charger location are would be a very easy install.

If you don't want to spend anything, just cancel or return the Rivian charger and use the mobile charger to the existing 6-50 with an adapter
This. 100%. With your panel that close, it’ll be peanuts to have the electrician install a 60 amp circuit and hardwire the Rivian EVSE so you get the fastest possible charge speed (my panel was in the basement, like 30ft from the install location). I’d also have the electrician change the 6-50 to a 14-50 to give you flexibility for that one time in your life when you absolutely have to charge two EVs at the same time. Just because it’s already there…
 

electruck

Well-Known Member
Joined
Oct 6, 2019
Threads
74
Messages
4,159
Reaction score
7,732
Location
Dallas, TX
Vehicles
2023 Rivian R1S
I stand corrected, thank you. 6/3 would only allow for 44a so you'd have to dial back the charger or go to 4/3.

THHN/THWN in conduit would be unnecessary extra work since the panel is recessed in drywall and the run would be inside the drywall.
Although I have seen one report of someone being able to force(?) 4 AWG wire into the terminals, the terminals are designed for a max of 6 AWG.

40A vs 48A charging isn't going to make that huge of a difference but if I were already having an electrician out to install a new circuit, I would go ahead and max out the EVSE. Patching drywall is not a big deal.
 

Christopher

Well-Known Member
First Name
Christopher
Joined
May 31, 2022
Threads
34
Messages
583
Reaction score
573
Location
South Florida
Vehicles
R1T
Occupation
Tech
Clubs
 
Although I have seen one report of someone being able to force(?) 4 AWG wire into the terminals, the terminals are designed for a max of 6 AWG.

40A vs 48A charging isn't going to make that huge of a difference but if I were already having an electrician out to install a new circuit, I would go ahead and max out the EVSE. Patching drywall is not a big deal.
That was me. I ran 4 AWG THWN just in case newer charger tech allowed for higher amperage in the future or if I wanted to run a sub panel and split it. Let me tell you it was a b**** to get those wires inside the Rivian charger but I got it done.
 

EarlyAdptr

Well-Known Member
First Name
Scott
Joined
Feb 17, 2021
Threads
17
Messages
429
Reaction score
579
Location
Seattle
Vehicles
Toyota Sequoia
Occupation
Consultant
For what it's worth, I struggled with this decision as well. I'm happy with my ultimate choice (Rivian Wall charger direct-wired to panel) but now that I've had my R1S the charging power of the NEMA circuit would have been more than capable. I've throttled my charge rate down to 30amps each night and it still only takes a few hours. I haven't really put much in the way of miles on the truck yet - so haven't stressed about range much - just my normal daily driving (~30 miles / day).
 

Cosmacelf

Well-Known Member
Joined
Nov 11, 2020
Threads
20
Messages
442
Reaction score
530
Location
San Diego, CA
Vehicles
Rivian R1S, Tesla Model X
Occupation
Software
Sorry but 6/3 NM-B (Romex) does NOT meet code (inadequate temp spec) and should NOT be used to wire a 48A EVSE. No competent electrician should be using Romex for this. 6 AWG THHN through conduit would be a proper install for a short run like that.

riv_evse_wire.png
Absolutely correct, the reason I said dont freak out if the electrician uses 6 gauge Romex for 60A is that a lot of electricians do that anyways. That rating is meant to protect installation for worse case scenarios like running Romex above the insulation in an attic that could hit 130 F in the summer. In a wall, many electricians wouldn’t see a problem using it, but you are correct that it isn’t code.

The easy correct thing to do is to use 6 gauge MC cable for 60A installs. More info about all of this here: https://carcharging.us/tech/install.php
 

Sponsored

rivianguy

Well-Known Member
Joined
Jun 10, 2022
Threads
39
Messages
257
Reaction score
680
Location
Seattle
Vehicles
Rivian R1S
Was hoping for advice on how to proceed with my charging set up.
I have a 6-50 outlet (50 amps).
I have a rivian wall charger that I am going to have an electrician install. Should I have him convert that outlet and use the wires for the wall charger (I guess this would cap wall charger at 40 amps - with proper adjustments) OR should I leave the outlet there and have him create a new 60a circuit and install the wall charger above that outlet (I park right in front of that area). Thanks for your input!

IMG_2127.JPG
I'd leave the one you have and get a new full 60 put in to max out the Rivian charger.
 

dekeen

Well-Known Member
First Name
David
Joined
May 30, 2022
Threads
4
Messages
111
Reaction score
79
Location
Raleigh, NC
Vehicles
Launch Edition R1S
Occupation
Consultant
Unless you need that current outlet for something else, I would just use that circuit and
swap the 6-50R for a 14-50R and set the dip switches on the Rivian wall charger to 40 amps. You won't notice the difference in charging speed. You are fine with a 50 amp circuit.
 

CommodoreAmiga

Well-Known Member
Joined
Dec 30, 2020
Threads
39
Messages
4,104
Reaction score
7,729
Location
INACTIVE
Vehicles
INACTIVE
Unless you need that current outlet for something else, I would just use that circuit and
swap the 6-50R for a 14-50R and set the dip switches on the Rivian wall charger to 40 amps. You won't notice the difference in charging speed.
Depends on the use case.

40A charging should get ~20 miles per hour range gained. That is sufficient for most, but I wouldn't say it's not noticeable.