What kind of wiring would you suggest? I just bought 75 feet of this 6/3 romex stuff, ran it and installed charger for my RAV4 EV - which will be fine. But I didn't run the other line for the Rivian yet. My line is about 30 feet (hince why I bought 75 feet for 2 lines). I've got a big enough box for both - brand new build and made sure of that.
6/3 romex can handle up to 55A or a 44A EVSE, but I don't know that you can find a 55A breaker or an EVSE that can be set to 44A. Practically speaking, you will have a 50A circuit that will support a 40A EVSE.
If you want to run the Rivian EVSE at 48A it will require a 60A circuit.
Sponsored

 

SANZC02

Well-Known Member
First Name
Bob
Joined
Feb 11, 2021
Threads
50
Messages
7,502
Reaction score
12,873
Location
California
Vehicles
Tesla Model S, LE - R1S
Occupation
Retired
What kind of wiring would you suggest? I just bought 75 feet of this 6/3 romex stuff, ran it and installed charger for my RAV4 EV - which will be fine. But I didn't run the other line for the Rivian yet. My line is about 30 feet (hince why I bought 75 feet for 2 lines). I've got a big enough box for both - brand new build and made sure of that.
6/3 Romex on a 50 AMP breaker is good for 40 amp charging, on a 60 amp Breaker it is good for 44 amps (there are no 55amp breakers so you can go up to the 60 but the line is only limited to the wire rating) 6AWG Romex is only rated at 55 amps so you can only go to 80% of that for a continuous load.

If you want to get the full 48 amps you need to go with 6AWG THHN in conduit on a 60 amp breaker.

EDIT: this is the section for the breaker
Rivian R1T R1S Qmerit - Rivian Home Charger Installation Experience 1631220923573
 

johnnylawson

Well-Known Member
First Name
John
Joined
Sep 6, 2020
Threads
23
Messages
220
Reaction score
454
Location
Cincinnati
Vehicles
2022 LE LG Rivian R1S, 2024 Volvo XC40 Recharge
Occupation
Director, Technical Architecture / Developer
Clubs
 
6/3 Romex on a 50 AMP breaker is good for 40 amp charging, on a 60 amp Breaker it is good for 44 amps (there are no 55amp breakers so you can go up to the 60 but the line is only limited to the wire rating) 6AWG Romex is only rated at 55 amps so you can only go to 80% of that for a continuous load.

If you want to get the full 48 amps you need to go with 6AWG THHN in conduit on a 60 amp breaker.

EDIT: this is the section for the breaker
1631220923573.png
Thanks - makes since. I have the 60 amp breaker so I just need to swap out my wire. Already was doing conduit. Thanks
 

lefkonj

Well-Known Member
First Name
Jeff
Joined
Feb 6, 2021
Threads
37
Messages
1,469
Reaction score
2,645
Location
New Jersey
Vehicles
Gen2 R1S Tri, I4-m50
Clubs
 
I needed 2 circuits moved to my sub panel, the 50AMP circuit pulled about 150 feet, and a module for my generator installed, cost me $2000
 

CommodoreAmiga

Well-Known Member
Joined
Dec 30, 2020
Threads
39
Messages
4,104
Reaction score
7,729
Location
INACTIVE
Vehicles
INACTIVE
Thanks - makes since. I have the 60 amp breaker so I just need to swap out my wire. Already was doing conduit. Thanks
AFAIK, you shouldn’t put NM (Romex) in conduit, anyway.
 

Sponsored

johnnylawson

Well-Known Member
First Name
John
Joined
Sep 6, 2020
Threads
23
Messages
220
Reaction score
454
Location
Cincinnati
Vehicles
2022 LE LG Rivian R1S, 2024 Volvo XC40 Recharge
Occupation
Director, Technical Architecture / Developer
Clubs
 
AFAIK, you shouldn’t put NM (Romex) in conduit, anyway.
I read about that and it was like 50/50 on the net if it was alright or not. I got 1 inch conduit to give it plenty of breathing room for the heat to escape out the top.
 

dfx

Well-Known Member
First Name
Dave
Joined
Nov 23, 2020
Threads
1
Messages
160
Reaction score
197
Location
Chicago
Vehicles
2001 LandCruiser, 2015 Model S 70D
I read about that and it was like 50/50 on the net if it was alright or not. I got 1 inch conduit to give it plenty of breathing room for the heat to escape out the top.
Wait--if you're running EMT why bother with Romex , just go with THHN
 

TessP100D

Banned
Well-Known Member
Joined
Feb 10, 2021
Threads
0
Messages
587
Reaction score
429
Location
So cal
Vehicles
Tesla 2017 P100D MS
don’t get me wrong. I wouldn’t do it myself. I will also add that I don’t have enough power to use the Rivian charger to its fullest abilities. I’m going to have to down rate it to 40 amps. If I wanted to get a full 100 amps to my garage it would cost a lot more money as I would have to rewire everything from the main to the subpanel. Not ready to do that yet
Part of owning an EV is upgrading your main service panel. Sub panel and all the stuff that is required to get the right voltage to your needed location. You will won’t care about the cost when you plug in every night and you won’t miss passing all the gas stations as you drive your bad ass RT1.
 

TessP100D

Banned
Well-Known Member
Joined
Feb 10, 2021
Threads
0
Messages
587
Reaction score
429
Location
So cal
Vehicles
Tesla 2017 P100D MS
I just did two at my house in Seattle. Quotes varied quite a bit, but outside of Seattle proper (technically unincorporated KC):
$100 to pull the permit.
$695 to install the EVSE for a 60 amp hardwire. Length of run that you need makes a different. I had to run my interior one to the opposite wall on the garage.
+$395 if you need to reconfigure the panel.

Edit: also, plan ahead. As with everything else, it seems like electricians are busy.
And you need to know exactly where you will park the truck and where the outlet will be. The cord is pretty short. Measure twice and cut once.
 

SeaGeo

Well-Known Member
First Name
Brice
Joined
Jan 12, 2021
Threads
50
Messages
5,673
Reaction score
10,212
Location
Seattle
Vehicles
Xc60 T8
Occupation
Engineer
And you need to know exactly where you will park the truck and where the outlet will be. The cord is pretty short. Measure twice and cut once.
I mean, most are 25 ft, but yeah plan it out.
 

Sponsored

CommodoreAmiga

Well-Known Member
Joined
Dec 30, 2020
Threads
39
Messages
4,104
Reaction score
7,729
Location
INACTIVE
Vehicles
INACTIVE
My original gen 1 Tesla wall charger has a 25’ cord. But all the. We ones are shorter. 20’ I think.
Tesla Wall Connector Gen 3 (current) has a 24' cable.
 

johnnylawson

Well-Known Member
First Name
John
Joined
Sep 6, 2020
Threads
23
Messages
220
Reaction score
454
Location
Cincinnati
Vehicles
2022 LE LG Rivian R1S, 2024 Volvo XC40 Recharge
Occupation
Director, Technical Architecture / Developer
Clubs
 
Wait--if you're running EMT why bother with Romex , just go with THHN
Right - but I already bought romex (and cut to length so no return), ran it for one charger. For the Rivian I'll get the THHN. Should of done the THHN the whole time but you learn as you go :)
 

Eeyore

Well-Known Member
First Name
Bruce
Joined
Nov 21, 2020
Threads
3
Messages
1,148
Reaction score
1,492
Location
Oregon
Vehicles
R1T LE, ID.4 AWD Pro S, Honda Fit
Occupation
Retired Union Electrician
Clubs
 
I ran 6/3 THHN wire which is rated for 75 amps at 90C.
Actually, you can't use 90C as your rating factor unless all the parts of the circuit also have a 90C rating. That includes the breaker, the outlet, and/or any wire terminating parts. If any 1 of those things is rated for only 70C, then the whole circuit can have the max ampacity that 70C can have.
 

flabyboy

Well-Known Member
Joined
Jul 3, 2021
Threads
3
Messages
341
Reaction score
501
Location
Minnesota
Vehicles
Mazda 6
Occupation
Health Care
Is it known how long the Rivian Wall chargers cable is?
Sponsored

 
 








Top