Has anyone had issues with faulty wall chargers that could have caused breakers to literally melt. Truck was set at 48A and was wired to spec. Reinstalled 50A breaker and dialed back to 40A. Breaker still gets slightly warm and very faint buzzing. Wondering if there are faulty wall chargers out there.

Rivian R1T R1S 60A breaker melted while charging BDE4DE7F-2661-479C-9C6A-6B35D68CC129
Sponsored

 

Electrified Outdoors

Well-Known Member
First Name
Ken
Joined
Jan 30, 2023
Threads
63
Messages
3,683
Reaction score
3,980
Location
Mount Airy, Maryland
Website
EVoutdoors.org
Vehicles
2024 Rivian R1S Quad, 2024 Silverado EV RST First Edition
Occupation
Real Estate
Clubs
 
Check for loose wiring. The breaker should not melt...it should trip and stop the current flowing when it heats up too much.
 

Revelation

Well-Known Member
Joined
Nov 28, 2018
Threads
4
Messages
288
Reaction score
500
Location
North Carolina
Vehicles
Rivian Blue R1T
Occupation
IT Solutions Architect
Agree with 240vPlug, likely a loose wire the resulted in arcing. Faulty breaker is possible, but less likely.
 

azbill

Well-Known Member
First Name
Bill
Joined
Jun 8, 2020
Threads
17
Messages
1,695
Reaction score
1,976
Location
Arizona
Vehicles
Escalade IQ, Mach E, Hummer EV SUT
Occupation
Retired
I had a 50A wall plug (14-50) melt like that. I found one of the hot wires was loose when I pulled the burnt plug from the wall box, that one wire just fell off. The other three wires were all tight. Likely the torque was not done properly on that screw. My breaker did eventually trip, but not until the plug was completely damaged.
 

mikehmb

Well-Known Member
First Name
Mike
Joined
Jan 12, 2022
Threads
154
Messages
2,303
Reaction score
5,223
Location
SF Bay Area
Vehicles
My name is Mike, and I have a (car) problem
Like @azbill I’ve had a NEMA14-50 melt like that.

Munro did a video where they showed a melted breaker, as well. It’s definitely not supposed to happen.



TL;DR of all of this is that duty cycles for residential applications seems to be inadequate for many charging applications. Get Commercial-rated plugs, if you’re using them, and always always make sure you reduce draw 20% from rated current on a hardwired connection.
 

Sponsored

mikehmb

Well-Known Member
First Name
Mike
Joined
Jan 12, 2022
Threads
154
Messages
2,303
Reaction score
5,223
Location
SF Bay Area
Vehicles
My name is Mike, and I have a (car) problem
I had a 50A wall plug (14-50) melt like that. I found one of the hot wires was loose when I pulled the burnt plug from the wall box, that one wire just fell off. The other three wires were all tight. Likely the torque was not done properly on that screw. My breaker did eventually trip, but not until the plug was completely damaged.
I had the same failure, with the same loose plug. I believe the heat cycling of the plug is what is ultimately loosening up the contactor, causing it to eventually arc and then superheat and fail.
 

VSG

Well-Known Member
Joined
Oct 3, 2022
Threads
4
Messages
3,210
Reaction score
6,006
Location
WA
Vehicles
R1T LE/RB/OC/20
I've had a socket melt from a vacuum cleaner. Point is, this is an electrical issue which just happened to occur on your EV charger circuit, but the problem isn't really about what you had connected to the circuit. My problem was a failed socket.

If something melts, that mean too much current went through it and it got too hot. The breaker is supposed to trip to prevent that, but if the current was diverted before the breaker, the breaker may not see that excess current.

If for example a wire connection is loose, or if the screw is tightened down on the wire insulation rather than the conductor itself (or if many other things), then the resistance at the connection will be high, meaning there will be power loss at the connection in the form of heat. That can be enough to melt things even if the total current never exceeded the breaker's limit.

Breaker getting slightly warm is expected, but buzzing tells me there's something vibrating, which could be an indication of something loose either at a wire connection or internally in a breaker.

If it were a faulty charger I would expect something in the charger would have melted first.

If you had an electrician install the charger, I would have them come out and fix the circuit for you because it appears something was done wrong.
 

Revelation

Well-Known Member
Joined
Nov 28, 2018
Threads
4
Messages
288
Reaction score
500
Location
North Carolina
Vehicles
Rivian Blue R1T
Occupation
IT Solutions Architect
To charge at 48A, you would need a 60A breaker. That could be the issue.
Based on the way the OP worded his post, I believe he had a 60A prior to the issue. Installed a 50A after and dialed back the charge rate to 40A on the EVSE. I could have misunderstood the OP, but that is my understanding.
 

rhesusraider

Active Member
Joined
Mar 8, 2022
Threads
0
Messages
26
Reaction score
35
Location
Massachusetts
Vehicles
R1S, Impreza, '65 Mustang
Based on the way the OP worded his post, I believe he had a 60A prior to the issue. Installed a 50A after and dialed back the charge rate to 40A on the EVSE. I could have misunderstood the OP, but that is my understanding.
Gotcha. That makes sense. Then I would definitely be concerned and thinking about the wiring. I should have read the title more carefully!
 
Last edited:

Sponsored

CharonPDX

Well-Known Member
First Name
Charon
Joined
Jul 12, 2021
Threads
31
Messages
2,499
Reaction score
4,172
Location
Cascadia
Vehicles
'22 R1T LE, '16 Model S, '19 Arcimoto FUV
Occupation
InfoSec Geek
Clubs
 
We had that happen with our very first EVSE - a 32A unit wired to a 40A circuit. The electrician used the existing wiring and breaker (was for a long-decommissioned electric water heater) and apparently it wasn't up to snuff. Had to replace both the breaker and the wiring with brand new.

But apparently the internal arcing damaged the busbar! The new one welded itself to the busbar after a few months. So if we ever need to replace that breaker, we'll have to replace the whole service panel.
 

TexasBob

Well-Known Member
First Name
Bob
Joined
Jan 15, 2022
Threads
49
Messages
1,193
Reaction score
2,641
Location
Houston
Vehicles
2024 R1T DM LRG, 2025 R1S Dune
Reiterating what other's have said, we had an overheating plug on a 60A circuit which melted the receptacle, turned out to be a loose wire.
 

nukem384

Well-Known Member
First Name
Darrell
Joined
Aug 30, 2021
Threads
2
Messages
148
Reaction score
132
Location
Bay Area, CA
Vehicles
Model 3/Rivian R1S
To charge at 48A, you would need a 60A breaker and 6 AWG line. That could be the issue. A 50A breaker could support 40A charging.
You can actually see in the OP post that the breaker is an Eaton Type BR 60a (on the burnt up label "BR 260"). As the other poster mentioned, OP changed it out to a 50a breaker after the fact to get by for now.
 

Supratachophobia

Well-Known Member
Joined
Apr 8, 2023
Threads
9
Messages
1,781
Reaction score
2,122
Location
Ohio
Vehicles
S
Clubs
 
Has anyone had issues with faulty wall chargers that could have caused breakers to literally melt. Truck was set at 48A and was wired to spec. Reinstalled 50A breaker and dialed back to 40A. Breaker still gets slightly warm and very faint buzzing. Wondering if there are faulty wall chargers out there.

BDE4DE7F-2661-479C-9C6A-6B35D68CC129.jpeg
That my friend, is a loose wire. Who wired it?
 

nfrank

Well-Known Member
First Name
Nathan
Joined
Sep 30, 2019
Threads
16
Messages
359
Reaction score
528
Location
Bay Area, CA
Vehicles
F-150
It's probably a loose wire, but I've also heard a lot of counterfeit breakers and electrical parts are hitting the market. Make sure you buy the replacement from a reputable parts distributor.

Also, if the wire is aluminum you need to use grease on the connection.