Aluminum is permitted by code for certain applications. It's still used frequently for service and subpanel feeds. But the terminal connections must be rated CU/AL (Copper/Aluminum). Most (all?) EVSE are probably not AL rated. The electrican could use a crimp on ferrule rated for AL->CU termination.
But AL must be a larger gauge for the same ampacity, so you get into other physical issues. #6 Copper THHN is rated at 75 amps, around 80 - 90 cents a foot. You need #4 AL THHN for the same 75 amps, around 55 - 65 cents a foot. Aluminum is cheaper, but not a 3x difference, assuming your electrician is buying at a true supply house and not Home Desperate. His quote seems......odd.
But AL must be a larger gauge for the same ampacity, so you get into other physical issues. #6 Copper THHN is rated at 75 amps, around 80 - 90 cents a foot. You need #4 AL THHN for the same 75 amps, around 55 - 65 cents a foot. Aluminum is cheaper, but not a 3x difference, assuming your electrician is buying at a true supply house and not Home Desperate. His quote seems......odd.