You need a new electrician. 6awg 90c thhn copper is rated to 75 amps.Here I go again,
Electrician asked me to speak to his supplier to clarify wire size. Supplier says 6AWG THHN is rated to 55 ampacity and for 48 A charging I need to go to 4AWG.
Here on the forum people have said that while the charger block may accept 4AWG The connection block is spec'd for 6AWG so don't do it.
Here People have said that 6 AWG THHN in conduit IS ok .
What am I missing? (and please don't say an electrician)
My current presumptive plan is 6AWG THHN in a flexible PVC Conduit. I an seeing that 6AWG ampacity is 65A and with a 20 percent derating for safety sould be fine carrying 52 A .
Thanks again in advance.
Maybe he is looking at 60c or maybe aluminum wire but seriously, I would not let that electrician anywhere near my house.