Electrical people. Opinions on this L2 Install?
Supratachophobia
Ohio
S
Some codes allow to round up as a 55 amp breaker is rare.
Personally I’m not a fan of rounding up as at some point the person installing that circuit will not be around and all people will see is the 60 amp breaker and thing that circuit is good for 48 amp continuous load. I’d prefer the 50 amp breaker so the lowest portion of that circuit is visible and not hidden in a wall.
+1. Rounding up to the next available size breaker should be allowed (I think a snippet from the code was posted above), but my personal risk appetite is closer to SANZC02, and if charging at 40a anyway, a 60a breaker isn't going to make a difference in the first place. I'm happy for it to trip if it hits 50.
While I certainly respect everyone's individual risk tolerances, at the end of the day, the code, which is designed with the express purpose of your house not burning down, says that it's okay to charge at 48 amps on a 60 amp breaker.
6-3 on a 60 amp breaker is what Tesla originally had in their Gen1 and Gen2 hpwc install instructions and I've personally never had an issue nor heard of an issue with a hardwired charger running under those conditions. I will add that they called for pure copper explicitly. Certainly more issues with improperly installed 14-50 outlets and mobile charger. And by issues, I mean garages and houses burning down.
ElGuano
Cali
I thought we were talking about 40 amp charging here. With 48 amps, it's not just "ok to charge with a 60amp breaker," you MUST have it due to breakers typically being rated for non-continouous load (or 80% of their rating for continuous load).
Supratachophobia
Ohio
S
Oh. OP still totally needs #6 for 40amps continuous. Is he considering 8? That's a hard no.
DucRider
Gary
ORegon
Polestar 2, Ioniq, R1S
Gen 1 installation manual:
NOTE: For most branch circuits of 100A, use 3 AWG (26.7 mm2), 75°C (167°F) copper wire. For installations less than 100A, use conductors that are sized according to local electrical codes
Gen 2:
Use conductors that are sized in accordance with local wiring regulations. The selected cable must be able to sustain periods of constant load of up to the maximum amperage selected by the electrician.
Rivian Owner
Pacific North West
1971 GTO, 2019 F150,
If you are going to spend the money to put a sub panel in the garage, why not size the panel large enough for future expansion? The wire, panel, and breakers may cost a little more but the labor costs won't change. If you have to put holes in walls or the ceiling that will need to be patched, it makes sense to spend a little more to get some added capacity. Considering that you may eventually upgrade to bi-directional (BiDi) charging the upgraded capacity will save having to replace what your electrician is going to install now.
SparkyR1t
Chicago
R1t/Model Y
Retired Commercial Electrician and mechanic
If you are putting in a sub panel, you might as well run something much bigger than 6
Agree if you’re doing a sub panel I would not go less than 100 amps for future growth. Also neutral and ground would be required but almost all wall connectors require a neutral or ground reference for circuitry and led lighting do it correctly and pull the extra conductor.
babock
Bruce
Los Angeles and South Lake Tahoe
2025 Rivian R1T, 2024 GMC Denali 2500HD, 2022 Hyundai SantaFe PHEV
Retired Electrical Engineer
Not all. None of my EV chargers(4 of them including 3 that plug into outlets) require neutral including the 240V input for the portable charger that comes with the Rivian.
teartags
Tim
Lyons, Colorado
R1T A/T
Wow, this got out of hand quick. Didn't know I'd get 3 pages of responses!
Nowhere in my original post did I mention a subpanel.
I am running 6-3 Romex to a shutoff in the garage
6AWG THHN in conduit from shutoff to Charger
It'll all be hooked to a 50 amp breaker
I will charge at 40 amps.
Thanks again all.
Electrified Outdoors
Mount Airy, Maryland
EVoutdoors.org
Real Estate
technically you need #4 if your running NMB Romex for the 60 amp circuit even though your only charging at 48 amps. THHN in conduit is the way to go for max safety if you want #6. Another option might be #6 MC but not sure if it meets code. Make sure you pull a permit and get it inspected to CYA.
babock
Bruce
My electrician just ran 6 AWG NMB romex. I was there when the city of Los Angeles building inspector signed off on it.
48A EV charger with 60 A breaker.
Sounds about right for LA...
Speaking from experience, you might (or might not) be surprised at how many inspectors don't know the NEC and will sign off without looking at the details. Other inspectors go the other direction - fail everything when they are in doubt, and make you prove otherwise.
The circuit needs to be 60A. The weakest link, #6 Romex, is not 60A.
EVoutdoors.org
Real Estate
It will probably be fine, and you have it permitted. Can’t tell you how many times I have seen this. They love running that 6/2 ROMEX. The funny thing is the Romex is rated for 90c just like the THHN but NEC requires ampacity derating to 60C which is why its ampacity is only 55 amps.