FWIW: My licensed electrician used the wrong cable type to support a sustained 48A charge. Specifically, he installed 6/2 Romex NM-B cable, which is only rated for 55A. Because EV charging is considered a continuous load, that cable can safely support 40A max, not 48A.

I had my Rivian EVSE DIP switch set to 48A, which over time (a year+) resulted in “warm plug” warning and derating issues. Thankfully, Rivian replaced it under warranty, even after they pointed out the wiring issues from photos they requested as part of a warranty claim.
Sponsored

 

babock

Well-Known Member
First Name
Bruce
Joined
Dec 6, 2024
Threads
5
Messages
141
Reaction score
111
Location
Los Angeles and South Lake Tahoe
Vehicles
2025 Rivian R1T, 2024 GMC Denali 2500HD, 2022 Hyundai SantaFe PHEV
Occupation
Retired Electrical Engineer
FWIW: My licensed electrician used the wrong cable type to support a sustained 48A charge. Specifically, he installed 6/2 Romex NM-B cable, which is only rated for 55A. Because EV charging is considered a continuous load, that cable can safely support 40A max, not 48A.
I have that same cable. I use 44A which is 80% of 55A.
 

dj200

Active Member
First Name
John
Joined
Jun 7, 2024
Threads
5
Messages
41
Reaction score
99
Location
Orange County, CA
Vehicles
G2-S-Quad, C8-Eray
Occupation
Engineer
Appreciate the feedback. It sounds like I could get away with a 100 amp panel, but it’s safer to go 200 amp.
I‘m running a 60 amp breaker in a 100 amp panel with no problems.
The charger is pulling 48 amps over 6 gauge wire with a length of 3 feet (Hard-wired). Never had any overheating problems.
If you are going to use a NEMA 14-50, then the max breaker size is 50 amps with the charger pulling 40.
Bottom line - the 100 amp panel should be fine. (Assuming your overall usage has “room”)
 
Last edited:

babock

Well-Known Member
First Name
Bruce
Joined
Dec 6, 2024
Threads
5
Messages
141
Reaction score
111
Location
Los Angeles and South Lake Tahoe
Vehicles
2025 Rivian R1T, 2024 GMC Denali 2500HD, 2022 Hyundai SantaFe PHEV
Occupation
Retired Electrical Engineer
I'm not sure I understand. In my case, I had to adjust the dip switches to 40A to prevent overheating again.
Thae max crrent that the AWG 6 Romex will support is 55A...as you stated. 80% of 55A is 44A.

With my Wallbox, I can set it from my app. Not that I am promoting wallbox, I hate it.

From the car's control panel, you can also limit it to 44A.
 
Last edited:

Sponsored

Time2Roll

Well-Known Member
Joined
Jul 10, 2025
Threads
2
Messages
811
Reaction score
697
Location
SoCal
Vehicles
2026 R1S Quad - 2001 F150
Beacuse romex is in a tight sheath The NEC derates it and it is not acceptle for 48 amps. 6awg in a conduit sheds more heat and is code complient. Despite this many electricians will use 6awg romex on a 60 A breaker to a 48 v charger.
50A outlet should have the EVSE set to 40A max.

Also 40A circuit is fine on 50A outlet with the EVSE limited to 32A. This may also reduce the load to avoid upgrading the main panel. 32A is about 13 - 15 miles per hour range on the Rivian.

Is this not a rental? Good luck with $3K to upgrade a main panel.
 
OP
OP
CampfireWisdom

CampfireWisdom

Well-Known Member
First Name
Greg
Joined
Mar 22, 2025
Threads
14
Messages
97
Reaction score
108
Location
Rancho Cucamonga, CA
Website
www.campfirewisdompodcast.com
Vehicles
2014 Toyota Prius C, 2018 Subaru Forester
Occupation
Teacher
I‘m running a 60 amp breaker in a 100 amp panel with no problems.
The charger is pulling 48 amps over 6 gauge wire with a length of 3 feet (Hard-wired). Never had any overheating problems.
If you are going to use a NEMA 14-50, then the max breaker size is 50 amps with the charger pulling 40.
Bottom line - the 100 amp panel should be fine. (Assuming your overall usage has “room”)
Excellent! I got room and was told about $4K for a new panel. As a renter, hell no. So, I’m going to do as you all recommended.

Hubbell 9450a
Metal conduit
6 ga THHN
50amp (I’m fine with 9.6)
$525 - I provide outlet & breakers
 

Kaiju

Well-Known Member
Joined
Aug 18, 2024
Threads
2
Messages
146
Reaction score
261
Location
Texas
Vehicles
R1T
Edit: Nevermind. If you're renting it makes no sense to pay yourself for the ugprade.

My house had a 200A service coming in but from the meter to the panel was only sized for around 150 and the panel itself was too small to accommodate the extra breaker (which was a code violation but hey). I did the math on my actual demand with certain things running and found out that yeah, I could trip the main if I was charging and certain other automatic things were running, particularly electric heat and the hot water boiler. I didn't want to have to manually manage that and didn't want to set the charger to only run at 20A.

There's also a point where if you make changes you'll have to bring everything up to current codes, which is a thing that can bite you if you're doing any sort of electrical work. I used the opportunity to not only match the 200A service coming in but completely replace the panel with a bigger one. Had to eat some extras to make everything compliant to the latest code, but it's not only futureproofing but avoids issues with either homeowners insurance demanding upgrades and potential issues with home inspections and quibbling if you sell.

I also used a Hubbell 9450A and put wire one gauge better than necessary in the wall, though it was actually a bit of a bear making the plug fit in the box because the wire was actually a bit too large/stiff to fit conveniently. I can't fault people for wanting to hardwire it, though personally I'm cool with charging at 40 amps and using the 50A plug/breaker combo. The plug has some extra utility and if I ever have problems with the charger it's just a matter of unplugging it and either using the portable one or getting another one. Or I can just take it with me places, though how convenient that is depends on which one you have.
 

Sponsored

HaveBlue

Well-Known Member
Joined
Nov 22, 2022
Threads
41
Messages
2,951
Reaction score
2,254
Location
91107
Vehicles
R1S DMP Max, Lifted GX470, APR Audi A7, BMW 325Ci
Clubs
 
To the OP, step one will be a load calculation by the electrician. He should be able to give you a print out. Step two will be to evaluate the panel whether it can support that load calculation as just the main breaker of 100A means little if it's a legacy panel. There are a lot of things to consider beyond wire. You might get lucky and have a nice empty panel that can support a 60A circuit. You might have some Zinsco burned bus where maybe a 14-30A is what should have gone in. For code reasons, many mobile 14-50 chargers only draw 32A and that is often pretty safe.
Rivian R1T R1S Got Electrician - What do I need to know? 2025-07-26 15.40.22
 

Rivian Owner

Well-Known Member
First Name
Mark
Joined
Sep 15, 2024
Threads
1
Messages
238
Reaction score
303
Location
Pacific North West
Vehicles
1971 GTO, 2019 F150,
Clubs
 
To the OP, step one will be a load calculation by the electrician. He should be able to give you a print out. Step two will be to evaluate the panel whether it can support that load calculation as just the main breaker of 100A means little if it's a legacy panel. There are a lot of things to consider beyond wire. You might get lucky and have a nice empty panel that can support a 60A circuit. You might have some Zinsco burned bus where maybe a 14-30A is what should have gone in. For code reasons, many mobile 14-50 chargers only draw 32A and that is often pretty safe.
2025-07-26 15.40.22.webp
Yeah I've seen the Zinsco burned bus on more than one panel. Without doing the load calcs, by code you can't put more load in a 100 amp box than 100 amps. I guess you can do it if you want to gamble on things like an insurance claim being denied, just like you can drive your Rivian without insurance and hope you don't get in an accident.

As a renter modifying the electrical without permitting, inspections, and work done by a licensed electrician, and approval from the landlord could expose you to a lifetime of debt or worse if things go wrong. Because someone on the web says it's ok, doesn't make it ok. If the work is permitted and signed off by the city you will be covered, anything short of city approval leaves you exposed, including after you move out.
 

HaveBlue

Well-Known Member
Joined
Nov 22, 2022
Threads
41
Messages
2,951
Reaction score
2,254
Location
91107
Vehicles
R1S DMP Max, Lifted GX470, APR Audi A7, BMW 325Ci
Clubs
 
Excellent! I got room and was told about $4K for a new panel. As a renter, hell no. So, I’m going to do as you all recommended.

Hubbell 9450a
Metal conduit
6 ga THHN
50amp (I’m fine with 9.6)
$525 - I provide outlet & breakers
That's the most reasonable way to go. Your code area may mandate a GFCI breaker for that outlet. You should consider looking for one that matches the panel. Two panel spaces will be needed for that otherwise the electrician will need some duplex or quad Plex replacements as well to make space. You'll need a deep outlet box that fits the 14-50; either a retrofit or surface mount. Several companies are making ev considered receptacles now as well.
Rivian R1T R1S Got Electrician - What do I need to know? 1000042077
Rivian R1T R1S Got Electrician - What do I need to know? 1000042078
 

Rade

Well-Known Member
First Name
Rade
Joined
Sep 19, 2024
Threads
38
Messages
644
Reaction score
813
Location
US - Rhode Island
Website
radmorningcoffee.blogspot.com
Vehicles
2025 Rivian R1T - Large. Delivered on November 23, 2024.
Occupation
Retired
I gave the Rivian charger specs to my electrician, and he took it from there.
 

Attachments

Oldsmobile_Mike

Well-Known Member
First Name
Mike
Joined
Mar 24, 2022
Threads
63
Messages
2,455
Reaction score
3,991
Location
Manassas Park, VA
Vehicles
FG/FE R1T recv'd 3/31/2023
Occupation
I build stuff
Clubs
 
use metal conduit
When I did mine, I didn't use conduit / armored cable. Granted, my install is only this far away from the garage sub-panel:

Rivian R1T R1S Got Electrician - What do I need to know? 1766522272249-o5


But now you've got me wanting to pull my wall board down and add it, LOL.