So a couple of things. Your electrician most likely calculated max nameplate amperage’s from all appliances and is assuming they will all be running continuously. If that equaled to 161 amps then he may have multiples by 25% assuming continuous duty which would require a service to the house of 201 amps
but what you really need is that total appliance amperage value but take into consideration the actual running time of all appliances whether 80% run time or sometime appliances only run 20% during the day or less
this is how a utility typically calculates a service rating requirement for a building. Actually is can be difficult and very expensive to move to a 400 amp service as the utility may have to upgrade cabling and transformers. Utilities will also ask for a load study as described above before considering a 400 amp service
with that said I see no reason you cannot add en EV wall connector. Especially if you schedule it to run in the off hours like late evemings. If you ever have the need for another wall connector pick one that can load share with the other one so they will auto reducing charging currents if two or more vehicle are connected at the same time
good luck
but what you really need is that total appliance amperage value but take into consideration the actual running time of all appliances whether 80% run time or sometime appliances only run 20% during the day or less
this is how a utility typically calculates a service rating requirement for a building. Actually is can be difficult and very expensive to move to a 400 amp service as the utility may have to upgrade cabling and transformers. Utilities will also ask for a load study as described above before considering a 400 amp service
with that said I see no reason you cannot add en EV wall connector. Especially if you schedule it to run in the off hours like late evemings. If you ever have the need for another wall connector pick one that can load share with the other one so they will auto reducing charging currents if two or more vehicle are connected at the same time
good luck