MountainBikeDude
Well-Known Member
- Thread starter
- #1
Afternoon all,
I've been having a problem for a while now and can't figure out the issue. When charging my R1T (only EV I have to test) my downstairs lights flicker.
Setup
I currently have 3 panels in my house, a main panel, with 200amp service. In that panel, I have a 60amp breaker for the Rivian charger 6' away. There is a 100amp sub panel beside it with all the downstairs breakers. Stove, WD, baseboards, etc including recessed LED pot lights throughout.
Another feed from the main runs upstairs to a second 100amp sub panel with all the same typical equipment /breakers including WD and HW.
The only lights that flicker are the ones running off the downstairs panel, and most noticeably, when they are dimmed to any degree. All upstairs lighting off the second sub panel don't seem to display the same issues.
My brother in law is an electrician and even he's having difficulty understanding the issue. He thinks it could be the feed from the pole causing it, but that should translate upstairs as well, which it's not.
We ran two experiments, one connecting the portable charger to the oven outlet, and the issue persisted. The second was lowering the output of the Rivian wall charger both from the truck, and then using the flip switches inside the EVSE. Same results from 3kW draw and up obviously the flickering was greater or more noticeable at 11.5kW or 48amp. And yes, we rebooted the wall charger so the jumper settings would take effect and limit it's output.
We checked the voltage, and it was holding steady, but unfortunately couldn't test the amperage.
He thought it might be the neutral wire not being connected, but then quickly realized they aren't needed.
If anyone has experienced the same or has any ideas, I'm all ears!
I've been having a problem for a while now and can't figure out the issue. When charging my R1T (only EV I have to test) my downstairs lights flicker.
Setup
I currently have 3 panels in my house, a main panel, with 200amp service. In that panel, I have a 60amp breaker for the Rivian charger 6' away. There is a 100amp sub panel beside it with all the downstairs breakers. Stove, WD, baseboards, etc including recessed LED pot lights throughout.
Another feed from the main runs upstairs to a second 100amp sub panel with all the same typical equipment /breakers including WD and HW.
The only lights that flicker are the ones running off the downstairs panel, and most noticeably, when they are dimmed to any degree. All upstairs lighting off the second sub panel don't seem to display the same issues.
My brother in law is an electrician and even he's having difficulty understanding the issue. He thinks it could be the feed from the pole causing it, but that should translate upstairs as well, which it's not.
We ran two experiments, one connecting the portable charger to the oven outlet, and the issue persisted. The second was lowering the output of the Rivian wall charger both from the truck, and then using the flip switches inside the EVSE. Same results from 3kW draw and up obviously the flickering was greater or more noticeable at 11.5kW or 48amp. And yes, we rebooted the wall charger so the jumper settings would take effect and limit it's output.
We checked the voltage, and it was holding steady, but unfortunately couldn't test the amperage.
He thought it might be the neutral wire not being connected, but then quickly realized they aren't needed.
If anyone has experienced the same or has any ideas, I'm all ears!