Charged my R1T today around 11 and around 1 my wife said she noticed a burning smell from the garage. Noticed the charging cable was extremely warm. Checked the outlet and saw the pic below.

For reference, I had an electrician install Siemens 240V/30A charger in 2018. Charged a clarity EV, Etron, Mach E, and R1T fine until today. Though I Should, i dont know the amperage of the breaker. Thats my fault. I just assumed a licensed electrician would choos the right amperage. What does everyone think the most likely culprit of this is? What Shoukd be my next steps?

Thanks

Rivian R1T R1S Burnt 240V outlet IMG_1438


Edit: just checked the panel and it’s a 50 Amp breaker
Sponsored

 
Last edited:

Dark-Fx

Well-Known Member
First Name
Brian
Joined
Jul 15, 2020
Threads
147
Messages
13,517
Reaction score
27,280
Location
Michigan
Vehicles
R1T, R1S, Livewire One, Sierra EV, R1S
Occupation
Engineering
Clubs
 
Poor connection at the melted terminal.
 

Polar

Well-Known Member
First Name
Scott
Joined
Feb 16, 2022
Threads
33
Messages
1,098
Reaction score
2,039
Location
WA
Vehicles
C40, LE CY R1S
Occupation
IT
Clubs
 
Most likely - bad outlet.

That melting is indicative of heat caused by a poor quality connection between the outlet and the plug.
Replace with a Hubbell and carry on - also observing the 80/20 rule (only use 80% of your breakers rated capacity).
 

rkalbiar

Well-Known Member
First Name
Ruben
Joined
Feb 21, 2022
Threads
32
Messages
393
Reaction score
306
Location
Oregon
Vehicles
2022 Rivian R1T , 2024 Rivian R1S
Agreed. Poor quality outlet. It happens, sadly.
 

rkalbiar

Well-Known Member
First Name
Ruben
Joined
Feb 21, 2022
Threads
32
Messages
393
Reaction score
306
Location
Oregon
Vehicles
2022 Rivian R1T , 2024 Rivian R1S
You can go Hubbell, the best. Or you can go Bryant 9450FR for virtually equivalent quality, also owned by Hubbell, but for much less moola.
 

Sponsored

evguy

Well-Known Member
Joined
Sep 20, 2022
Threads
6
Messages
370
Reaction score
585
Location
Orange County, CA
Vehicles
'22 R1S LE; '18 Model 3 LR; '26 IONIQ 5 SEL
Occupation
Law
Yep, bad connection in the outlet (possibly resulting from years of plugging and unplugging chargers), happened to me in my old garage. Hardwired EVSE is the way to go if you want to avoid this in the future.
 

Electrified Outdoors

Well-Known Member
First Name
Ken
Joined
Jan 30, 2023
Threads
63
Messages
3,683
Reaction score
3,980
Location
Mount Airy, Maryland
Website
EVoutdoors.org
Vehicles
2024 Rivian R1S Quad, 2024 Silverado EV RST First Edition
Occupation
Real Estate
Clubs
 
This is why I always recommend a hardwired installation for a permanent home EV charger. The contactors inside of these outlets wear out, especially if you plug and unplug it frequently. It's an additional failure point and hardwiring allows you to eliminate that failure point as well as a GFCI breaker. It also has the added benefit of charging at 48 amps versus 40.

If you can, I would replace that with a hardwired EV charger. Preferably a 60 amp circuit as well. If not, you can just hardwire up a charger to the 50 amp circuit and eliminate that receptacle.

There are some folks that insist on having The 14-50 outlet and in that case an industrial grade outlet is highly recommended.

When these outlets were first designed, they were never designed for the very long continuous loads of electric vehicle charging. Electrician s usually put in cheap off-the-shelf outlet and those just aren't up to the task.
 

Zoidz

Well-Known Member
First Name
Gil
Joined
Feb 28, 2021
Threads
226
Messages
5,185
Reaction score
11,685
Location
PA
Vehicles
23 R1S Adv, Avalanche, BMWs-X3,330cic,K1200RS bike
Occupation
Engineer
What was the charging rate set at? For a 30A circuit you should be charging at no more than 24A.
 

HaveBlue

Well-Known Member
Joined
Nov 22, 2022
Threads
41
Messages
2,926
Reaction score
2,234
Location
91107
Vehicles
R1S DMP Max, Lifted GX470, APR Audi A7, BMW 325Ci
Clubs
 
Check the wire size and type. From the look of that BX cable I'll guess it's only #10 which is to small for that 50A breaker. If was rated for 50A then now would be a good time to put in a 14-50 or better yet hard wire a unit and set it to the correct amperage. Likely the other cars with smaller batteries never charged as long also.
 

Hercules10

Well-Known Member
First Name
Gregory
Joined
Aug 8, 2023
Threads
2
Messages
85
Reaction score
79
Location
San Antonio
Vehicles
R1S
Occupation
Retired
Clubs
 
I have a Rivian charger with a direct connect to a 240 box. The approved wiring gets warm at 48amps, so I backed it down to 38 amps charging at night. Constant expansion and contraction of the wiring can loosing the wiring nuts. So good to check them every so often.
 

Sponsored

Proxy

Well-Known Member
First Name
Me
Joined
Nov 11, 2023
Threads
2
Messages
198
Reaction score
224
Location
Ventura County
Vehicles
R1T R1S
Occupation
Professional
Probably did not get installed correctly. I have the proper tool to torque everything correctly. However, I have never seen an electrician use anything other than plain old tools using their “calibrated” forearm.
 

YouKnowWhatsUp

Banned
Well-Known Member
Joined
Mar 7, 2024
Threads
7
Messages
105
Reaction score
100
Location
Valley Village CA
Vehicles
‘24 R1T Limestone
Even on my hardwired Tesla charger I needed the wires tightened after a year. It’s good to check the connections on the charger and the breaker yearly and tighten them. Breakers and outlets are relatively cheap until they melt and damage wires.
 

azbill

Well-Known Member
First Name
Bill
Joined
Jun 8, 2020
Threads
17
Messages
1,695
Reaction score
1,976
Location
Arizona
Vehicles
Escalade IQ, Mach E, Hummer EV SUT
Occupation
Retired
I had this exact thing happen. When I took the cover off and pulled the plug out, one of the wires just fell out. It was due to a loose connection, the electrician obviously did not torque it correctly.
 
OP
OP

Ngkgb

Well-Known Member
Joined
Feb 7, 2022
Threads
82
Messages
829
Reaction score
770
Location
United States
Vehicles
Rivian R1T
Should I have lowered the amperage in the truck? From my understanding, the charger and the truck work together to figure out the maximum it can charge.
Sponsored

 
 